gas insulated substation full report
#10
[attachment=9908]
INTRODUCTION
Conventional substations requires, small installation size, protection against atmospheric pollution and moisture, noiseless operation, nonexplosive and flame resistant, reduced maintenance, minimal radio interference, but totally enclosed substations using SF6 gas as insulation that are also known as GIS is now in widespread use in the electrical power industry .
It consist of :
It consist of Bus bars Circuit breakers Disconnecting switches Earthing switches Current transformers Voltage transformers Densimeter Cable and boxes Gas supply and gas monitoring equipment Local control
Circuit Breaker :
Circuit Breaker Under short circuit conditions, however, the current may reach tens of thousands of amperes at a power factor as low as 0.1. It is duty of a circuit breaker to interrupt such currents as soon as possible to avoid equipment damage.
Disconnectors :
Disconnectors Disconnectors or isolators are used for electrical isolation of circuit parts They are slow acting and operating at off load Disconnectors must be carefully designed and tested to be able to break small charging current without generating too-high over voltage,
Local Control Cubicles “LCC” :
Local Control Cubicles “LCC” LCC is the interface cubicles to all secondary systems of a substation which are represent a station control and protection. LCC includes control and alarm functions as well as the correct distribution of auxiliary power supply for the relevant GIS bay.
Earthing Switch :
Earthing Switch Slow-operating earthing switch are used for protection purpose when work is being done in the substation, but are operated only when it is certain that the high-voltage system is not energized. The fast-closing earthing switch can close against full voltage and short circuit power. The high speed earthing switch is achieved by means of a spring-closing device.
Voltage Transformer :
Voltage Transformer Variable location on feeder and busbars. Integrated disconnecting facility for GIS and power cable testing without dismantling and gas handling.• Flexible gas compartment allocation for optimal service oriented gas supervision.•
Current Transformer :
Current Transformer in the single phase enclosed Core of• CT is located outside the enclosure$inside for three phase Gas compartment to reduce access of moisture and to suppress gas-tight bushings for secondary connections.•
Cables Compartment :
Cables Compartment 1. Optimized solution for plug-in type power cable connection. 2. Adjustable support structures for minimum requirements for the GIS floor. 3. Fixation to the GIS floor by cemented anchor bolts, no need for special foundation (steel beams….etc)
PROPERTIES OF SF6 :
PROPERTIES OF SF6 SF6 does not harm to the ozone layer. Sf6 gas is chemically stable Non poisonous Colourless&heavier than air Almost water insoluble Non inflammable
ADVANTAGES :
ADVANTAGES Gis have no risks for fire&explosion due to leakage of oil They generate no noise&have no radio interference Located closure to load centers there by reducing transmission&distribution s\ms It offer solutions including -In industrial areas where space&pollution problems -Mountain areas where ice&snow are major problems
DISADVANTAGES :
DISADVANTAGES GIS installations tend to be much more expensive that air-insulated installations with the same rating. VFTO during switching operations or earth faults and transient enclosure voltages and particle contamination
APPLICATIONS :
APPLICATIONS High voltage installations (above 115kv) Urban installations Indoor installations
Comparison b\w gis&ais :
LAY OUT OF GIS :
GAS INSULATED TRANSFORMER :
GAS INSULATED TRANSFORMER Use SF6 Gas as the insulating and cooling medium instead of insulating oil. First units produced in 1967. Transformer applications: Distribution class units up to 400 MVA, 345 kV. •Primarily used in substations located in urban areas (including inside buildings, underground) due to safety benefits.
GAS INSULATED SWITCH GEAR :
GAS INSULATED SWITCH GEAR The space occupied by switch gear is greatly reduced Totally unaffected by atmospheric conditions Provides high degree of operational reliability Easier to install in difficult site conditions
GAS INSULATED SHUNT REACTOR :
GAS INSULATED SHUNT REACTOR Features Suitable for installation Excellent history of reliability and safety Fine radial core Circular yoke and circular tank Low loss Easy maintenance Manufacturing Range Voltage-13.8 ~ 138kV Frequency-50 or 60Hz Capacity-5 ~ 60Mvar
FUTURE TRENDS IN GAS INSULATED SUBSTATIONS :
FUTURE TRENDS IN GAS INSULATED SUBSTATIONS Compact design of switch gear by using three phase modules Use of vacuum circuit breaker cells in the medium high voltage GIS and fewer brakes per pole in high voltage circuit breakers Optimization of GIS design to allow easier maintenance
Reply

Important Note..!

If you are not satisfied with above reply ,..Please

ASK HERE

So that we will collect data for you and will made reply to the request....OR try below "QUICK REPLY" box to add a reply to this page
Tagged Pages: http seminarprojects org t gas insulated substation full report page 4, gas insulated substation pdf report, gas insulated substation ppt, seminar on gas insulated switchgear substation, gas insulated substation pdf seminar, gas insulated substation full report, gas insulated substation full report ppt,
Popular Searches: ieee based gas insulated substations, seminar paper on gas insulated substations, gas insulated substation pdf e books free, gas insulated transmission lines wikipedia, gas insulated substation project abstract**at are the top 10 books, lossless transmission through gas insulated conductors, picture of air insulated substation ppt,

[-]
Quick Reply
Message
Type your reply to this message here.

Image Verification
Please enter the text contained within the image into the text box below it. This process is used to prevent automated spam bots.
Image Verification
(case insensitive)

Messages In This Thread
RE: gas insulated substation full report - by seminar class - 10-03-2011, 09:55 AM
RE: gas insulated substation full report - by Guest - 27-12-2012, 07:46 AM
RE: gas insulated substation full report - by Guest - 06-08-2013, 01:14 PM

Possibly Related Threads...
Thread Author Replies Views Last Post
  man made sun full report seminar presentation 2 3,445 26-12-2014, 05:39 AM
Last Post: Guest
  microprocessor based system of automatic synchronizer full report computer science technology 10 8,580 05-09-2014, 10:44 PM
Last Post: seminar report asees
  artificial intelligence techniques in power systems full report computer science technology 3 5,733 08-08-2014, 10:39 PM
Last Post: seminar report asees
  thermoelectric power generation full report project report tiger 8 8,268 07-03-2014, 07:43 PM
Last Post: Guest
  powerline communication full report computer science technology 15 16,876 02-09-2013, 11:28 AM
Last Post: computer topic
  Four-Quadrant Control of Switched Reluctance Motors full report seminar topics 3 5,221 14-05-2013, 01:16 PM
Last Post: Guest
  MODELLING OF TRANSFORMER full report seminar class 2 3,861 11-04-2013, 11:44 AM
Last Post: computer topic
  CONDITION MONITORING OF TRANSFORMERS full report smart paper boy 4 3,370 22-02-2013, 02:23 PM
Last Post: seminar details
  protection of transmission lines using gps full report computer science technology 9 19,992 16-10-2012, 01:25 PM
Last Post: seminar details
  Variable Voltage And Variable Frequency drives full report seminar presentation 2 5,682 04-10-2012, 12:20 PM
Last Post: seminar details

Forum Jump: