Digital Testing of High Voltage Circuit Breaker
#1

INTROUCTION



ESSENTIAL QUALITIES OF HV CIRCUIT BREAKER

High-voltage circuit breaker play an important role in transmission and distribution systems. They must clear faults and isolate faulted sections rapidly and reliably. In-short they must possess the following qualities.

" In closed position they are good conductors.
" In open position they are excellent insulators.
" They can close a shorted circuit quickly and safely without unacceptable contact erosion.
" They can interrupt a rated short-circuit current or lower current quickly without generating an abnormal voltage.

The only physical mechanism that can change in a short period of time from a conducting to insulating state at a certain voltage is the arc.

With the advancement of power system, the lines and other equipment operate at very high voltages and carry large currents. High-voltage circuit breakers play an important role in transmission and distribution systems. A circuit breaker can make or break a circuit, either manually or automatically under all conditions viz. no-load, full-load and short-circuit conditions. The American National Standard Institute (ANSI) defines circuit breaker as: "A mechanical switching device capable of making, carrying and breaking currents under normal circuit conditions and also making, carrying for a specified time, and breaking currents under specified abnormal circuit conditions such as those of short circuit". A circuit breaker is usually intended to operate infrequently, although some types are suitable for frequent operation.


HISTORY

The first circuit breaker was developed by J.N. Kelman in 1901. It was the predecessor of the oil circuit breaker and capable of interrupting a short circuit current of 200 to 300 Ampere in a 40KV system. The circuit breaker was made up of two wooden barrels containing a mixture of oil and water in which the contacts were immersed. Since then the circuit breaker design has undergone a remarkable development. Now a days one pole of circuit breaker is capable of interrupting 63 KA in a 550 KV network with SF6 gas as the arc quenching medium.

THE NEED FOR TESTING

Almost all people have experienced the effects of protective devices operating properly. When an overload or a short circuit occurs in the home, the usual result is a blown fuse or a tripped circuit breaker. Fortunately few have the misfortune to see the results of a defective device, which may include burned wiring, fires, explosions, and electrical shock.

It is often assumed that the fuses and circuit breakers in the home or industry are infallible, and will operate safely when called upon to do so ten, twenty, or more years after their installation. In the case of fuses, this may be a safe assumption, because a defective fuse usually blows too quickly, causing premature opening of the circuit, and forcing replacement of the faulty component. Circuit breakers, however, are mechanical devices, which are subject to deterioration due to wear, corrosion and environmental contamination, any of which could cause the device to remain closed during a fault condition. At the very least, the specified time delay may have shifted so much that proper protection is no longer afforded to devices on the circuit, or improper coordination causes a main circuit breaker or fuse to open in an inconvenient location.
Reply

Important Note..!

If you are not satisfied with above reply ,..Please

ASK HERE

So that we will collect data for you and will made reply to the request....OR try below "QUICK REPLY" box to add a reply to this page
Popular Searches: seminar on circuit breaker maintance by mobiel softwear, password circuit breaker, pdf for digital testing of high vtg ckt breaker, digital testing of high voltage circuit breaker wiki, digital testig of high voltage circuit breaker ppt, abstract and conclusion for digital testing of high voltage circuit breakers, circuitbreakers,

[-]
Quick Reply
Message
Type your reply to this message here.

Image Verification
Please enter the text contained within the image into the text box below it. This process is used to prevent automated spam bots.
Image Verification
(case insensitive)

Messages In This Thread
Digital Testing of High Voltage Circuit Breaker - by project topics - 03-04-2010, 07:31 PM

Possibly Related Threads...
Thread Author Replies Views Last Post
  Electric field Optimization of High Voltage Electrode Based On Neural Networks computer science crazy 2 10,314 01-01-2018, 11:56 AM
Last Post: dhanabhagya
  Adaptive piezoelectric energy harvesting circuit for wireless remote power supply electronics seminars 3 4,580 18-02-2016, 02:18 PM
Last Post: seminar report asees
  A Neural-Network-Based Space-Vector PWM Controller for Voltage-Fed Inverter Inducti project report helper 1 9,120 07-09-2015, 06:23 PM
Last Post: hafsa_012
  Digital Audio's Final Frontier-Class D Amplifier computer science crazy 2 2,643 01-10-2014, 11:14 PM
Last Post: seminar report asees
  Digital Watermarking computer science crazy 4 3,901 05-09-2014, 09:27 PM
Last Post: seminar report asees
  Circuit Breaker Maintenance by Mobile Agent Software Technology project topics 16 14,076 23-04-2014, 08:27 PM
Last Post: Guest
  High Performance Motor Drive Using Matrix Converter project topics 3 9,650 27-07-2013, 10:35 AM
Last Post: computer topic
  Voltage Stability Improvement using Static Var Compensator in Power Systems project report tiger 4 13,578 12-07-2013, 11:29 AM
Last Post: computer topic
  Voltage Swell and Overvoltage Compensation Wifi 2 9,471 12-07-2013, 10:50 AM
Last Post: computer topic
  Fault Locating In Undegrounded And High Resistance GroundedSystems computer science crazy 12 14,791 15-04-2013, 02:15 PM
Last Post: Guest

Forum Jump: