gas insulated substation full report
#1

[attachment=2351]

GAS INSULATED SUBSTATION

INTRODUCTION

Conventional substations requires, small installation size, protection against atmospheric pollution and moisture, noiseless operation, nonexplosive and flame resistant, reduced maintenance, minimal radio interference, but totally enclosed substations using SF6 gas as insulation that are also known as GIS is now in widespread use in the electrical power industry .
It consist of
¢ Bus bars
¢ Circuit breakers
¢ Disconnecting switches
¢ Earthing switches
¢ Current transformers
¢ Voltage transformers
¢ Densimeter
¢ Cable and boxes
¢ Gas supply and gas monitoring equipment
¢ Local control

Circuit Breaker

Under short circuit conditions, however, the current may reach tens of thousands of amperes at a power factor as low as 0.1. It is duty of a circuit breaker to interrupt such currents as soon as possible to avoid equipment damage.

Disconnectors

¢ Disconnectors or isolators are used for electrical isolation of circuit parts
¢ They are slow acting and operating at off load
¢ Disconnectors must be carefully designed and tested to be able to break small charging current without generating too-high over voltage,

Local Control Cubicles LCC

LCC is the interface cubicles to all secondary systems of a substation which are represent a station control and protection.
LCC includes control and alarm functions as well as the correct distribution of auxiliary power supply for the relevant GIS bay.

Earthing Switch

Slow-operating earthing switch are used for protection purpose when work is being done in the substation, but are operated only when it is certain that the high-voltage system is not energized. The fast-closing earthing switch can close against full voltage and short circuit power. The high speed earthing switch is achieved by means of a spring-closing device.

Voltage Transformer

Variable location on feeder and busbars.
¢ Integrated disconnecting facility for GIS and power cable testing without dismantling and gas handling.
¢ Flexible gas compartment allocation for optimal service oriented gas supervision.

Current Transformer

¢in the single phase enclosed Core of CT is located outside the enclosure$inside for three phase
¢ Gas compartment to reduce access of moisture and to suppress gas-tight bushings for secondary connections.

Cables Compartment

1. Optimized solution for plug-in type power cable connection.
2. Adjustable support structures for minimum requirements for the GIS floor.
3. Fixation to the GIS floor by cemented anchor bolts, no need for special foundation (steel beams¦.etc)

PROPERTIES OF SF6


¢ SF6 does not harm to
the ozone layer.
¢ Sf6 gas is chemically stable
¢ Non poisonous
¢ Colourless&heavier than air
¢ Almost water insoluble
¢ Non inflammable

ADVANTAGES

¢ Gis have no risks for fire&explosion due to leakage of oil
¢ They generate no noise&have no radio interference
¢ Located closure to load centers there by reducing transmission&distribution s\ms
¢ It offer solutions including
-In industrial areas where space&pollution problems
-Mountain areas where ice&snow are major problems

DISADVANTAGES

GIS installations tend to be much more expensive that air-insulated installations with the same rating.
VFTO during switching operations or earth faults and transient enclosure voltages and particle contamination

APPLICATIONS

¢ High voltage installations (above 115kv)
¢ Urban installations
¢ Indoor installations

GAS INSULATED TRANSFORMER

Use SF6 Gas as the insulating and cooling medium instead of insulating oil.
First units produced in 1967.
Transformer applications: Distribution class units up to 400 MVA, 345 kV.
¢Primarily used in substations located in urban areas (including inside buildings, underground) due to safety benefits.

GAS INSULATED SWITCH GEAR

The space occupied by switch gear is greatly reduced
Totally unaffected by atmospheric conditions
Provides high degree of operational reliability
Easier to install in difficult site conditions

GAS INSULATED SHUNT REACTOR

Features
¢ Suitable for installation
¢ Excellent history of reliability and safety
¢ Fine radial core
¢ Circular yoke and circular tank
¢ Low loss
¢ Easy maintenance
Manufacturing Range
¢ Voltage-13.8 ~ 138kV
¢ Frequency-50 or 60Hz
¢ Capacity-5 ~ 60Mvar

FUTURE TRENDS IN GAS INSULATED SUBSTATIONS

Compact design of switch gear by using three phase modules
Use of vacuum circuit breaker cells in the medium high voltage GIS and fewer brakes per pole in high voltage circuit breakers
Optimization of GIS design to allow easier maintenance

CONCLUSION

GIS are necessary for EHV&UHV and some important areas to be studied include more conservative designs better particle control&improved gas handling&decomposition product management techniques
Achieving&maintaining high levels of availability requires a more integrated approach to quality control by both users and manufactures
Reply

Important Note..!

If you are not satisfied with above reply ,..Please

ASK HERE

So that we will collect data for you and will made reply to the request....OR try below "QUICK REPLY" box to add a reply to this page
Tagged Pages: conclusion of gas insulated substation, ppt gas insulated substation full report, gas insulated substation seminar report pdf, seminar report on gas insulated substation pdf, gas insulated substation, gas insulated substation full seminar report download, gas insulated substation pdf report,
Popular Searches: gas insulated substation seminar report pdf, gas insulated transmission lines full report, gas insulated substation abstrct, gas insulated substation project abstract, gas insulated substations by ms naidu free download e book, advantages of gas insulated sub stations ppt, lossless transmission through gas insulated conductors,

[-]
Quick Reply
Message
Type your reply to this message here.

Image Verification
Please enter the text contained within the image into the text box below it. This process is used to prevent automated spam bots.
Image Verification
(case insensitive)

Messages In This Thread
gas insulated substation full report - by project report tiger - 19-02-2010, 11:46 AM
RE: gas insulated substation full report - by Guest - 27-12-2012, 07:46 AM
RE: gas insulated substation full report - by Guest - 06-08-2013, 01:14 PM

Possibly Related Threads...
Thread Author Replies Views Last Post
  man made sun full report seminar presentation 2 3,445 26-12-2014, 05:39 AM
Last Post: Guest
  microprocessor based system of automatic synchronizer full report computer science technology 10 8,580 05-09-2014, 10:44 PM
Last Post: seminar report asees
  artificial intelligence techniques in power systems full report computer science technology 3 5,733 08-08-2014, 10:39 PM
Last Post: seminar report asees
  thermoelectric power generation full report project report tiger 8 8,268 07-03-2014, 07:43 PM
Last Post: Guest
  powerline communication full report computer science technology 15 16,876 02-09-2013, 11:28 AM
Last Post: computer topic
  Four-Quadrant Control of Switched Reluctance Motors full report seminar topics 3 5,221 14-05-2013, 01:16 PM
Last Post: Guest
  MODELLING OF TRANSFORMER full report seminar class 2 3,861 11-04-2013, 11:44 AM
Last Post: computer topic
  CONDITION MONITORING OF TRANSFORMERS full report smart paper boy 4 3,370 22-02-2013, 02:23 PM
Last Post: seminar details
  protection of transmission lines using gps full report computer science technology 9 19,992 16-10-2012, 01:25 PM
Last Post: seminar details
  Variable Voltage And Variable Frequency drives full report seminar presentation 2 5,682 04-10-2012, 12:20 PM
Last Post: seminar details

Forum Jump: